18" B16.5 Blind flange needs drilled and tapped to accept a 1.5" PSV
WeldEng0318
Industrial
Hi everyone,
I have class 300 18" blind flange bolted to a manway. We are proposing to do a 1.5" drill and tap and thread a PSV in. My assumption was to follow Table 6 and 8 but they are a bit confusing as to weather its allowed or not because i feel like its not really addressing my exact question? Any input would be appreciated
Thank you
I assume you are referring to B16.5 table 6. This gives the smallest hole (attached pipe) that requires reinforcing. If attached pipe is smaller you can attached it without a flange hub or reinforcing
But only in the centre ...
There are many posts on this issue. Do a search.
At LI: iirc some time ago an interpretation was posted saying it may also be out of centre….
Huub
- You never get what you expect, you only get what you inspect.
Thanks. Exactly that one.
Huub
Thanks, forgot about that one.
Requesting some clarification here on this interpretation.
Question: The Interpretation does not "prohibit" an offset hole in blind flange. However, if the hole is offset, will the blind flange w/ fitting be considered altered and still need to be qualified per code?
Probably ought to be another thread?
As I read the interpretation, I don’t see how it requires additional consideration or qualification of any kind.
Huub
Begs the question: How FAR offset? [dazed]
Mike
I would say you can offset it as long as it meets note 1:
1) The hub dimensions shall be at least as large as those of the standard flanges of the size to which the reduction is being made, except flanges
reducing to a size smaller than those of columns 2, 4, and 6 may be made from blind flanges
so in other words, if you are reducing to a 1/2" NPS, X = 1.19 per table 8C, so as long as you have a 0.155" ((1.19-0.88)/2) to the nearest hub edge on a 150# hubbed blind, you are ok. If it's a standard blind, then as long as the reduction is within the pressurized diameter.