David Deck Guy
Structural
- Aug 18, 2023
- 35
I am installing a roof deck on a Chicago building built in 1942. I have about 13.3 kips of allowable load that I need to dump on a brick wall. I'm trying to ascertain the lower bound f'm of the material. 11.2.3.10 Default Properties of ASCE 41-17 says that if I can scrape the mortar away with a metal utensil, I need to consider it to be lime mortal and will have to use a compressive strength of 285 psi. Yikes. When I go back to the site to confirm thickness of wall and scrape at mortar, even if it doesn't easily scrape away, I'll still be hesitant to use anything higher because I assume that the walls have been tuckpointed in the last 80 years. Does anyone have any tips on how to eek out a few hundred more psi from this brick? Right now I'm looking at a 24" x 8" bearing plate for my pocketed beam, and that assumes the wall is 12" thick which is not guaranteed.
Also, if I have to use f'm=285psi, I assume this means I'd have to scale my capacity for post installed dewalt or hilti anchors, which means I probably should give those companies a call tomorrow.
Finally, in searching the forums for past posts on this topic, I came across references to the book "Structural Analysis of Historic Buildings: Restoration, Preservation, and Adaptive Reuse Applications for Architects and Engineers." Is there anyone that has this book and recommends it?
Also, if I have to use f'm=285psi, I assume this means I'd have to scale my capacity for post installed dewalt or hilti anchors, which means I probably should give those companies a call tomorrow.
Finally, in searching the forums for past posts on this topic, I came across references to the book "Structural Analysis of Historic Buildings: Restoration, Preservation, and Adaptive Reuse Applications for Architects and Engineers." Is there anyone that has this book and recommends it?