1960s era joist 3
CUTiger1989
8
Working on a job in South Carolina to determine capacities of existing joists. Most I have had to measure and search the historical SJI tables.
But, for one gymnasium we have drawings that specify a 60G22 steel joist for the roof framing. The span is approximately 101'-0". They are spaced at 8'-0" o.c. I have yet to find a table or manufacturer for the 60G22.
If any of you can point me in the right direction, it would be greatly appreciated.
 https://files.engineering.com/getfile.aspx?folder=5c4c730b-8fbd-4dd1-9a7d-8f38f6d724b8&file=20230405_111513.jpg
Thank you for the replies!
@jerseyshore
Like you, I suspected the 'G' designation meant 'girder'. However, there are no joists framing into it. So, I did contact SJI. They were stumped as well.
@hokie66
I will give Vulcraft a try.
@robyengIT
Thank you for your reply.
I actually have that catalog from another school project I worked on. Unfortunately, the Haven-Busch joists have WT sections as top and bottom chords. The joist I am looking at now have double angle top and bottom chords.
@JAE
Looking at the top/bottom chord sections for the GWS joist do match what I observed in the field. Interesting that they used hat sections for the chords. I don't believe I have ever seen that.
The way it was explained to me was that the joist manufacturers will guarantee capacity (230/110), section properties (12K3), etc., whatever you specify, but they'll make them out of whatever they have that day. Angles, hats, T's, etc.
It makes them a joy to work with.
True conversation:
Me; "We specified 110/220, but they want to put a AHU on there, what's the capacity?"
Joist Guy; "It's good for 110 lb./ft. live load and 220 lb. per foot total load."
Me; "Yeah, but it must have a little margin?"
Joist guy; "It's good for 110 lb./ft. live load and 220 lb. per foot total load."
Me; "I have your calculations, but they're indecipherable. How can I figure out the section properties?"
Are the drawings with the notations shop drawings or design drawings? Is it possible the G is actually a different letter on an old print?
Don't be too shocked that they were spec'd by the architect. Back in the 60s there were likely quite a few architects that could remember when structural engineers didn't really exist - at least not in a form that we'd recognize today. The architect did it all.
I can't make heads or tails of the designation, either. You'll probably have to use detailed field survey data to do a complete analysis of the joist.
It's a little blurry, but it does look like 60G22. Are they 60 inches deep?
You'll probably just have to do a typical survey like pham said and see if SJI can find a close comparable.