SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
[F] 905.3.4 Stages. Stages greater than 1,000 squre feet in area shall be equipped with a Class III wet standpipe system with 1 1/2" and 2 1/2 inch hose connections on each side of the stage."
The building is fully sprinkled but the project engineer specified 2 1/2 inch hose connections wanted to be safe.
My question has to do with calculating the water supply.
The entire complex has but two 2 1/2 inch hose connections both at the stage. The theare itself does not have standpipes.
I am thinking the total demand would be 500 gpm and not 750 gpm.
Where do I start calculations or, more to the point, where is my "end head"? I don't calculate through the 2 1/2 inch pipe, do I? If I don't calculate the 250 gpm through the 2 1/2 inch pipe dropping down to the hose valves then do I start at the 4 inch x 2 1/2 inch overhead tee?
For for both comes from a dedicated 4" overhead line supplied by a fire pump.
Thanks.