Dilawar amjad
- Mar 4, 2019
- 12
We are using a the subject motor in seamless tube mill piercer application, the specs of the same are as under.
armature voltage: 930 volts dc
Base speed: 393 RPM
Motor rated current are 3600A at 300 RPM on 720 volts, 2830A at 393 RPM and 930 volts
Imax is twice on both above conditions.
Field Current: 120 Amperes
We have been in operation from the last couple of months, and the motor is being driven by Simatics DCM (Siemens) 7600 Amperes single quadrant drive with four thyristor stacks of 1900 amperes each.Recently we are having some fault having code F60038 (Overspeed threshold overshot) a couple of time in a day. The maximum speed for positive direction of rotation (p50380) of master drive is set on 150%, while that of negative direction of rotation(p5083) is set on 150% and this above setting for other three slaves are set on 200% for both postive and negative direction of rotation. The motor current is set on 70% of drive rated current i.e. 5320 amperes.
Kindly give your valuable advice for this remedy.
Best Regards
Base speed: 393 RPM
Best Regards
