2 Speed Motor Overloads

Status
Not open for further replies.

donaldschexnaider

Electrical
Oct 8, 2014
4
Replacing a set of 2 speed motor starters. The motors are two speed one winding (2S1W) motors. In the high speed the low speed motor T leads are shorted.
Question is the placement of the overloads specifically on the low speed leads. Should the low speed overloads see the current of the low speed leads while in high speed?
This is strictly in question as to where to pick off for the shorting of the low speed leads.
 
Replies continue below

Recommended for you

Yes there are a ton of these diagrams and schematics across the internet. None of them really approach the reasoning of the lo speed overloads while in the hi speed operation.
 
Look at the current paths - no current can pass through the low speed overload relay when the fast (K1) and shorting (K3) contactors are closed and the low speed contactor is open. Am I mis-understanding your question?
 