I have a major problem. I have a 2 story Ordinary Steel Braced frame with the second floor having a 5" thick concrete deck & a braced roof. Someone, however, altered the building by cutting some braces in the transverse direction of the building at both levels. I've been ordered to find a solution to this but the simplest of re-attaching the braces is out. Next solution would be to add light frame shear walls (top level) & CMU Shear wall(lower level) at the exterior along the grid lines where the braces have been cut. This would be the new lateral system. ASCE 7-05 & 2010 California Building Code require that I design my shear walls using R, omega, and Cd of an OSCBF since there are steel braces left intact. Using values for an ordinary system, however, results in Higher seismic forces. I also noticed that ASCE section 12.2.3.1 allows me to use a two stage analysis as long as the lower portion of my structure is 10x stiffer than the upper portion, period of upper portion shall be 1.1x greater than the total period, & the upper portion shall be flexible. Doing this I believe would require that the we get rid of all the braces in order to replace them with the new CMU & wood shear wall system which also allows me to use seismic forces generated by an R=5 & R=6.5.
Now in order to have a flexible upper level compared to the (E)lower concrete deck & (N)CMU SW, and be able to design for lower seismic forces. Would it be right to suggest that the remaining steel braces in the upper level be cut so that I can design for a more flexible upper section having wood shear walls(R=6.5 compared to R=3.25 of an OSBF)? Or can I keep my steel braces and just design wood shear walls for R=6.5 at the grid lines w/o braces per ASCE sec.12.2.3.2 "horizontal combination" and is the dual combination of wood SW along with Steel Braced frames allowed?
First floor is 9ft high & total height is 29ft this gives me a Ta=0.2499sec(total) & Ta=0.1891sec(upper level) doing 1.1Ta(upper)=0.208sec < 0.2499(total) using ASCE approximate method so I don't think I can use ASCE sec.12.2.3.2 two stage analysis unless I do a dynamic analysis to show that the periods are ok. Or by me using a stiffer lower (CMU Shear Wall) portion mean that I can automatically use wood shear walls in the upper level with out having to comply ASCE Vertical & horizontal combination requirements as it is done when designing a two story residence with a CMU or Concrete lower level and light frame upper? The building is also symmetrical w/o any irregularities.
Hopefully someone here can help.
Now in order to have a flexible upper level compared to the (E)lower concrete deck & (N)CMU SW, and be able to design for lower seismic forces. Would it be right to suggest that the remaining steel braces in the upper level be cut so that I can design for a more flexible upper section having wood shear walls(R=6.5 compared to R=3.25 of an OSBF)? Or can I keep my steel braces and just design wood shear walls for R=6.5 at the grid lines w/o braces per ASCE sec.12.2.3.2 "horizontal combination" and is the dual combination of wood SW along with Steel Braced frames allowed?
First floor is 9ft high & total height is 29ft this gives me a Ta=0.2499sec(total) & Ta=0.1891sec(upper level) doing 1.1Ta(upper)=0.208sec < 0.2499(total) using ASCE approximate method so I don't think I can use ASCE sec.12.2.3.2 two stage analysis unless I do a dynamic analysis to show that the periods are ok. Or by me using a stiffer lower (CMU Shear Wall) portion mean that I can automatically use wood shear walls in the upper level with out having to comply ASCE Vertical & horizontal combination requirements as it is done when designing a two story residence with a CMU or Concrete lower level and light frame upper? The building is also symmetrical w/o any irregularities.
Hopefully someone here can help.