2005 NEC section 215.2A1

Status
Not open for further replies.

mpparent

Electrical
Sep 26, 2001
399
Does anyone find this new section a bit confusing as I do?? It talks about the "grounded conductor", but the tables referenced are the "equipment grounding conductor".

Mike
 
Replies continue below

Recommended for you

No. Please read the commentary if you have the Handbook of NEC 2205, which explains it.

Basically, its a new requirements ensuring minimium size of the neutral (grounded) condcutor not less than the EGC.
 