milwaukeebob
Electrical
- Jun 21, 2004
- 42
Hello,
I have a question related to NEC Table 310.60(C)(77) “Ampacities of Three Single-Insulated Copper Conductors in Underground Electrical Ducts (Three Conductors per Electrical Duct) Based on Ambient Earth Temperature of 20°C (68°F), Electrical Duct Arrangement in Accordance with Figure 310.60(C)(3)..."
I’m involved with a project that has two (2) large 3 phase xfmrs installed. Each xfmrs primary side cabling is installed in underground (UG) ductbank and consists of three (3) 15kV, MV-90 rated cables per phase (gauge unimportant for this question). This UG ductbank for both xfmrs for the majority of the run is arranged in a configuration “similar” to detail 3 of NEC Figure 310.60(C)(3) – six (6) electrical ducts in a 2Hx3W arrangement. One additional important not is that proper spacing of the ducts was not adhered to during the installation.
When both xfmrs are energized and loaded, it's clear to me that NEC Table 310.60(C)(77) “Six Circuits” section is applicable for determining the ampacity of all the installed cables. The “Six Circuits” section shows a lower ampacity than the “Three Circuits” section which make sense because there’s a further derating required because of the impact of the extra heat from the cables in the added ducts.
My question is related to the scenario when only one of the xfmrs is energized and loaded with the other one out of service. In this scenario and with the configuration of the plant, the remaining xfmr will carry the full load and the other xfmr primary side circuit/cabling will be de-energized and not seeing any current flow. How does this get evaluated with regard to Table 310.60(C)(77)? It’s understood the ductbank is still six (6) electrical ducts in a 2Hx3W arrangement but now only one set of cables in three (3) of the ducts is flowing current and giving off heat. In this case, would the ampacity for these cables now be taken from the “Three Circuits” section of Table 310.60(C)(77) or does the Code still consider this a “Six Circuit” installation?
Thanks for any help and guidance on this.
I have a question related to NEC Table 310.60(C)(77) “Ampacities of Three Single-Insulated Copper Conductors in Underground Electrical Ducts (Three Conductors per Electrical Duct) Based on Ambient Earth Temperature of 20°C (68°F), Electrical Duct Arrangement in Accordance with Figure 310.60(C)(3)..."
I’m involved with a project that has two (2) large 3 phase xfmrs installed. Each xfmrs primary side cabling is installed in underground (UG) ductbank and consists of three (3) 15kV, MV-90 rated cables per phase (gauge unimportant for this question). This UG ductbank for both xfmrs for the majority of the run is arranged in a configuration “similar” to detail 3 of NEC Figure 310.60(C)(3) – six (6) electrical ducts in a 2Hx3W arrangement. One additional important not is that proper spacing of the ducts was not adhered to during the installation.
When both xfmrs are energized and loaded, it's clear to me that NEC Table 310.60(C)(77) “Six Circuits” section is applicable for determining the ampacity of all the installed cables. The “Six Circuits” section shows a lower ampacity than the “Three Circuits” section which make sense because there’s a further derating required because of the impact of the extra heat from the cables in the added ducts.
My question is related to the scenario when only one of the xfmrs is energized and loaded with the other one out of service. In this scenario and with the configuration of the plant, the remaining xfmr will carry the full load and the other xfmr primary side circuit/cabling will be de-energized and not seeing any current flow. How does this get evaluated with regard to Table 310.60(C)(77)? It’s understood the ductbank is still six (6) electrical ducts in a 2Hx3W arrangement but now only one set of cables in three (3) of the ducts is flowing current and giving off heat. In this case, would the ampacity for these cables now be taken from the “Three Circuits” section of Table 310.60(C)(77) or does the Code still consider this a “Six Circuit” installation?
Thanks for any help and guidance on this.