Cidona
Mechanical
- Oct 21, 2007
- 147
The 2010 edition of NFPA 13 has section 7.1.2.1, which states 'Relief valves will be required on all wet pipe systems that do not have auxilary air reservoirs. Previously, they were only required on gridded systems. The size of the relief valve was increased to 1/2" and the relief valve now needs to be listed'.
I thought I heard that the reason for the relief valve on all wet systems was because there was something in there that was going to require that the air be expelled from the system when filling. And that therefore due to the lack of air in the system to act as a cushion for the expansion and contracton with temperture flucuation, that the relief valve was now required.
However, I can't see anything in '10 requiring any provisions for removing air from the system. 8.17.4.2.4 allows the inspectors test anywhere after the WFS, so they're not trying to enforce it that way. Anyone see anything more in this regards?
I thought I heard that the reason for the relief valve on all wet systems was because there was something in there that was going to require that the air be expelled from the system when filling. And that therefore due to the lack of air in the system to act as a cushion for the expansion and contracton with temperture flucuation, that the relief valve was now required.