The 4' offset is shown on one level. I don't see anywhere indicating that it has to stack over the one below. In fact, figure R602.10.8(2) suggests that the wall panels do not have to stack. The only mention of them having to stack that I can find is Section R602.10.2.1 which references R602.3.5 stating that the braced wall panels must stack if they provide a wind uplift path for the roof framing.
Does that mean that braced wall lines (say interior walls) don't have to have to align or even be within 4' floor-to-floor?
The 4' offset is shown on one level. I don't see anywhere indicating that it has to stack over the one below. In fact, figure R602.10.8(2) suggests that the wall panels do not have to stack. The only mention of them having to stack that I can find is Section R602.10.2.1 which references R602.3.5 stating that the braced wall panels must stack if they provide a wind uplift path for the roof framing.