Zeeko83
Civil/Environmental
- Apr 30, 2010
- 17
Please help me to understand this footnote b in table 601.
"Except in Group F-1, H, M and S-1 occupancies, fire protection of structural members shall not be required, including protection of roof framing and decking where every part of the roof construction is 20 feet or more above any floor immediately below. Fire-retardant-treated wood members shall be allowed to be used for such unprotected members." note b, Table 601.
1-Does that mean other groups such as (A-4 occupancy) does not require fire protection even if the height is less than 20 ft?
2-Does that means group F-1,H,M,S-1 does not require fire protection if height is more that 20 ft?
Thanks in advance.
"Except in Group F-1, H, M and S-1 occupancies, fire protection of structural members shall not be required, including protection of roof framing and decking where every part of the roof construction is 20 feet or more above any floor immediately below. Fire-retardant-treated wood members shall be allowed to be used for such unprotected members." note b, Table 601.
1-Does that mean other groups such as (A-4 occupancy) does not require fire protection even if the height is less than 20 ft?
2-Does that means group F-1,H,M,S-1 does not require fire protection if height is more that 20 ft?
Thanks in advance.