SprinklerDesigner2
- Nov 30, 2006
- 1,262
We are all aware of this
My question has to do with the IBC and ANSI A17.1 whch I do not have a copy of.
Building is a newly built four story motel that the building professional of record has called for a NFPA #13R system.
From what I have researched is it even possible to construct an elevator shaft with cars that are not ANSI A17.1 compliant? Maybe I am all wrong and wet but I find it very hard to believe it would even be possible and stay IBC compliance.
If the shaft and cars are ANSI A17.1 compliant does it even matter if hydraulic fluids are used?
The way I read it is if the shaft and car is compliant with ANSI A17.1 then sprinklers are never required at the bottom of the shaft.
Am I correct?
The next issue has to do with elevators per NFPA #13
The key words are "combustible hydraulic fluids".
I heard that some elevator companies are moving to non-combustible hydraulic fluids and I am wondering if this is rare, prevalent or becoming more prevalent?
How many hydraulic elevators are using non-combustible fluids?
Anyone have much experience with such issues?
NFPA 13R - 2013 Edition said:6.6.6* Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling unit ventilation equipment, crawl spaces, floor/ceiling spaces, noncombustible elevator shafts where the elevator cars comply with ANSI A17.1, Safety Code for Elevators and Escalators, and other concealed spaces that are not used or intended for living purposes or storage and do not contain fuel-fired equipment.
Am I correct?
NFPA #13 - 2013 Edition said:8.15.5.2 The sprinkler required at the bottom of the elevator hoistway by 8.15.5.1 shall not be required for enclosed, noncombustible elevator shafts that do not contain combustible hydraulic fluids.