Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

216-49 Wire Mesh 2

Status
Not open for further replies.

hawkaz

Structural
Oct 28, 2010
409
0
0
US
Looking at plans from 1955 where they call out one way CIP slab reinforcing as "216-49 wire mesh"

Does anyone have literature on this type of mesh?

Thanks in advance
 
Replies continue below

Recommended for you

It might be a grid with W4 at 2 inches and W9 at 16 inches, especially if the wires spaced at 2 inches are in the direction of the span. I think that there was a lot more flexibility in ordering custom sizes a long time ago.
I've attached the "Manual of Standard Practice for the Structural Welded Wire Reinforcing." If you can't decipher the grid from it, there's a phone number that someone might answer.
 
 https://files.engineering.com/getfile.aspx?folder=46a01724-f724-4d2f-97cf-88f54b37cc12&file=Manual_of_Standard_Practice_Structural_Welded_Wire_Reinforcement.pdf
In case anyone is interested, the wire institute responded:

The 216 refers to spacing in inches of the longitudinal and transverse wires, respectively, while the 49 refers to wire gauge of the longitudinal and transverse wires, respectively.

In this case, the style represents 4 gauge wires spaced at 2” on center and 9 gauge wires in the orthogonal direction at 16” oc.

This gives: 4ga @ 2” oc = 0.239 in2/ft, and 9ga @ 16” oc = 0.013 in2/ft

As you would probably surmise, it is most likely that the 4ga @ 2” oc is serving as the flexural reinforcement running parallel to span direction of the one-way slab over its supports, while the much lighter wire pattern is transverse and perhaps provided some (very) nominal shrinkage & temperature benefit.

Note that tensile and yield strength of the material back in this time period was in the 75 ksi and 65 ksi range, respectively.
 