230V-50Hz tools running on 208V-60Hz 1

Status
Not open for further replies.

ciao1982

Civil/Environmental
Feb 9, 2020
1
Hello,
my office is relocating me from Nairobi to Santo Domingo, and I am planning to put in the container all my garage tools (I am a hobbyist, doing on my free time mostly wood-steel furniture, but I have quite a few workshop machines). I have many single-phase electric tools 230V-50Hz, and a couple of three phase equipment 400V-50Hz.
In Santo Domingo I will have a house with 3 phases, so 120/208V-60Hz, and using the voltage between two phases, I am planning to equip my garage with an surface mounted electrical system having single phase at 208V-60Hz on the new garage sockets, so to be able to run my 230-50Hz tools. Regarding my machines which use 3 phases motors I am looking for suggestions, and please let me know also if you have any observations on the single-phase arrangement.
Thanks
 
Replies continue below

Recommended for you

Larger tools (e.g. table saw) often have motors that could be very easily replaced.


 
#1 Respecting the V/Hz ratio you will be about 75% of design voltage at 208 Volts, 60 Hz.
The V/Hz ratio at 230/50 is 4.6 Volts per Hertz.
4.6 Volts per Hertz at 60 Hz is 276 Volts.

400 Volts star = 230 Volts at 50 Hz, Again you need 276 Volts.

Lets see, a transformer rated for 240V/60V as an auto-transformer boost will give 300 Volts.
Connected to 208 Volts will develop 260 Volts.
That is about 6% below our target voltage.
At full current your motors will slide down the curve a little and develop a little more slip. (Run a few RPM slower.)

Solution: Two 4:1 lighting transformers connected in open delta will give you 260 Volts single phase and three phase.
Rating: Determine the maximum current expected. (Disregard starting currents.) That will be the current rating of the transformer secondaries.
So, a 5 KVA transformer will have a 60 Volt winding rated for 83 Amps. As an auto-transformer this transformer will support a 260 Volt load of 60 Amps x 260 Volts = 15.6 KVA.
WARNING: for three phase loads use the current. Do not attempt to add the KVA ratings. There is a reason.
Problem: A 240V/60V transformer may not be available.
Solution: Use a 480V/120V transformer. Again the size will be determined by the expected current on the 120 Volt winding.
You do know that your motors will run 120% faster, but with almost the same torque.
If your chosen transformers have taps you can get the voltage even closer.
Good luck.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
For starters, all your motors are going to be spinning at 20% more speed. While the motors probably can handle the higher speed, can the tools and other equipments connected to the motors handle it?

Muthu
 
Motors are relatively easy to deal with. Some of the mechanical limits may not be. Woodworking machines often have high spindle speeds - be very cautious about increasing the speed of anything such as a planer-thicknesser or a spindle moulder. If possible look at changing pulley sheaves to restore the normal operating speed. A cutting head burst will be messy.
 