textex
Computer
- Jun 2, 2021
- 7
Noob. I am trying to cost-optimize a branch circuit for a remote light display with a circuit distance of about 500 feet. US NEC applies. The remote lights will be commodity 120v equipment*, up to 1500W power required. My hope is to wire this with a 240V (split phase) buried branch circuit and a small transformer. Compared to a typical 120V branch circuit, this configuration allows 4x distance with the same voltage drop and power. Under these assumptions, 12 awg copper (~$.705/foot currently) is acceptable for the 240 circuit, versus 4 awg AL (~$1.90/foot) for a conventional 120v circuit.
My question has to do with what the NEC allows. Is it permissible to use an adequately-rated small transformer to serve a receptacle load? (If not, is it okay if the loads are hard-wired?) I could use an isolating 240-120V step-down transformer with 3-conductor branch circuit (with EGC), referencing one of the secondary sides to the primary (split-phase) neutral, with the EGC unbonded. This seems straightforward, but probably not cost effective.
Hopefully, I could use 2-wire cable (with EGC) and an autotransformer (such as Hammond 170J). I think (but not sure) this would be wired with one of the split phase legs straight through to the receptacle "hot" as well as a one of the outer terminals on the autotransformer. The other split phase leg would go to the second outer terminal. The receptacle neutral would wire to the center of the transformer. The EGC would be unbonded. My understanding is that the neutral would float with respect to the ground, but be close. Can this be made NEC compliant, if not for receptacle then for hard-wired loads?
*It may be possible to use all 240V compatible loads via European to Nema 6-15 plug adapter but...Nah
My question has to do with what the NEC allows. Is it permissible to use an adequately-rated small transformer to serve a receptacle load? (If not, is it okay if the loads are hard-wired?) I could use an isolating 240-120V step-down transformer with 3-conductor branch circuit (with EGC), referencing one of the secondary sides to the primary (split-phase) neutral, with the EGC unbonded. This seems straightforward, but probably not cost effective.
Hopefully, I could use 2-wire cable (with EGC) and an autotransformer (such as Hammond 170J). I think (but not sure) this would be wired with one of the split phase legs straight through to the receptacle "hot" as well as a one of the outer terminals on the autotransformer. The other split phase leg would go to the second outer terminal. The receptacle neutral would wire to the center of the transformer. The EGC would be unbonded. My understanding is that the neutral would float with respect to the ground, but be close. Can this be made NEC compliant, if not for receptacle then for hard-wired loads?
*It may be possible to use all 240V compatible loads via European to Nema 6-15 plug adapter but...Nah