Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

24DH11 3

Status
Not open for further replies.

jike

Structural
Oct 9, 2000
2,160
Does someone have an old joist table (not SJI) for these particular joists? I need to know capacities for a 40' span.
 
Replies continue below

Recommended for you

I have the SJI 60-year joist manual. Any idea what year the joist might have been made?
 
I have the 60 year jopist manual too, and there are no DH joists shown. Are you sure they are not DLH?

Is this the nomenclature on the joist tag?

FYI, 24" DLH11 is not listed either as they start at 52".

A 24" LH11 is good for 768/418 at 40 feet with a safe load of 31,200#. (total load / live load)

Your nomenclature must be wrong.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
No, these are NOT standard SJI joists. Thanks guys for your efforts, but the standard SJI tables are of no help.

The designation is correct and I remember seeing tables of a particular manufacturer that used to make these to get an advantage over their competition that did not have these available. The capacities must be gotten out of the specific manufacturer's tables.

The year of the joists was 1969. I am thinking it might be Armco or Sheffield.
 
Did you check sliderule's site?

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
It's bad when you can't remember what you recommended in the past. Old timer's disease...

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
We have a Sheffield Open Web Steel Joists (Armco Steel) Catalog #1565 (1966). It does not list a 24DH11, but does list a 24LH11. So that manufacture can't be it.

We also have a Ceco Deep Shortspan Steel Joists Catalog A.I.A. File No. 16-A (1967). It does list a 24DH11. "DH" Series Joists are fabricated from hot-rolled high strength steel sections having a minimum yield point of 50,000 psi. The design of these joists are based on allowable stress in tension of 30,000 psi. Ceco "DH" Series Open-Web Steel Joists are designed in accordance with the "H" Series specifications of the Steel Joist Institute.

Please see attachement for catalog pages.

Hope this helps.
 
 http://files.engineering.com/getfile.aspx?folder=f833ed16-e5bf-4d9e-b2fb-83502764c557&file=Ceco_Deep_Shortspan_Steel_Joists_Catalog_1967.pdf
I also am looking at an odd joist designation from Armco. The building is supposed to have been built in 1976. The tag from the joist shows J116 32 DH 10 21, ARMCO STEEL CORP

I downloaded the Ceco manual but they do not go to 32DH.

The joists are 4-ft o.c., current design snow load is 100-psf and should have been that in '76. The joists span approx 29-ft. This is a school building and I have mechanical equipment additions at several different roof areas.

Any help would be appreciated.
 