Dear all,
I'm checking a quote for a 25 kV Disconnector Switch and I noticed that in the attached circuit diagram the manufacturer uses 230 V AC (Europe) for all circuits, namely for the Control box auxiliaries (heating, light bulb, socket), the control circuit, the motor circuit and the signals to the remote terminal unit (Disconnector is located outdoor in an overhead circuit).
1) I can understand that with the above mentioned circuit we reduce cost by one cable that would have been used to carry the auxiliary voltage for the motor circuit , the control circuit and the the signals to the remote terminal unit (eg 48 V DC or 110 V DC ). According to your experience, are there any potential problems in using only 230 V AC instead of 230 V AC & 48 V DC or 110 V DC?
2) The 230 V AC enters the 25 kV Disconnector Switch Control box and directly feeds the auxiliaries, i.e. the heater, without an intervening a power switch, see the attached photo. The circuit breaker -Q11 located inside the control box protects the motor and control circuits. However, in the event of a fault in the heater or light bulb, we lose the 230 V AC of the disconnector (the remote circuit breaker shall trip). Is this configuration generally acceptable? Does it make sense to lose control of the Disconnector Switch for a short circuit in a heater or a light bulb?
Thank you very much!
I'm checking a quote for a 25 kV Disconnector Switch and I noticed that in the attached circuit diagram the manufacturer uses 230 V AC (Europe) for all circuits, namely for the Control box auxiliaries (heating, light bulb, socket), the control circuit, the motor circuit and the signals to the remote terminal unit (Disconnector is located outdoor in an overhead circuit).
1) I can understand that with the above mentioned circuit we reduce cost by one cable that would have been used to carry the auxiliary voltage for the motor circuit , the control circuit and the the signals to the remote terminal unit (eg 48 V DC or 110 V DC ). According to your experience, are there any potential problems in using only 230 V AC instead of 230 V AC & 48 V DC or 110 V DC?
2) The 230 V AC enters the 25 kV Disconnector Switch Control box and directly feeds the auxiliaries, i.e. the heater, without an intervening a power switch, see the attached photo. The circuit breaker -Q11 located inside the control box protects the motor and control circuits. However, in the event of a fault in the heater or light bulb, we lose the 230 V AC of the disconnector (the remote circuit breaker shall trip). Is this configuration generally acceptable? Does it make sense to lose control of the Disconnector Switch for a short circuit in a heater or a light bulb?
Thank you very much!