For the distribution power system protection engineers:
I am investigating 25kV distribution faults on an overhead system. A known fault occurred downstream of a recloser, which was downstream of the substation breaker on a radial distribution system (see ASCII SLD below).
[SUB BKR]-------[???2nd FAULT??]------------[Dx RECLOSER]---------------[KNOWN FAULT, TREE]---[LARGE CUSTOMER]
The fault occurred downstream of a the distribution recloser, but the substation relay locked out the breaker.
According to my TCC, there is at least 0.3s of separation between the sub bkr and the electronic recloser (both phase and gnd curves).
So, this should not have miscoordinated, but it did.
When looking at the waveforms recorded at the substation, there appeared to be very large fault currents that could not exist at the location of the tree. There is no generation on this radial line.
It appears that another fault occurred upstream of the Dx RECLOSER. The voltage measured at the sub dropped significantly, and even went to 0.1Vpu, which could not have occurred for the fault at the known location. And, the fault levels are much too high for a fault at the known location. Has anyone seen anything like this before?
Next steps we will take include downloading event data from the Dx RECLOSER and confirming that it was in service. We are also considering a line inspection at the suspected second fault location.
I am investigating 25kV distribution faults on an overhead system. A known fault occurred downstream of a recloser, which was downstream of the substation breaker on a radial distribution system (see ASCII SLD below).
[SUB BKR]-------[???2nd FAULT??]------------[Dx RECLOSER]---------------[KNOWN FAULT, TREE]---[LARGE CUSTOMER]
The fault occurred downstream of a the distribution recloser, but the substation relay locked out the breaker.
According to my TCC, there is at least 0.3s of separation between the sub bkr and the electronic recloser (both phase and gnd curves).
So, this should not have miscoordinated, but it did.
When looking at the waveforms recorded at the substation, there appeared to be very large fault currents that could not exist at the location of the tree. There is no generation on this radial line.
It appears that another fault occurred upstream of the Dx RECLOSER. The voltage measured at the sub dropped significantly, and even went to 0.1Vpu, which could not have occurred for the fault at the known location. And, the fault levels are much too high for a fault at the known location. Has anyone seen anything like this before?
Next steps we will take include downloading event data from the Dx RECLOSER and confirming that it was in service. We are also considering a line inspection at the suspected second fault location.