Proposed design is for an isolated phase arrangment consisting of 25kV cables with 3-500 kcmils and a #4/0 ground routed underground embedded in conduit.
there is no ferrorous, or steel encircling only one phase, but rebar around the entire duct bank.
The cables are shielded with a tape shield and was thinking that the shield will get hot because it encircles the conductors similar to rebar or steel. will that happen? last time i did one of these is was bussing from a generator.
also i don't believe the equipment ground is required to be in each conduit but can be run in a seperate conduit or exposed in the duct bank
thoughts?