27TN protection for a 150MW power generator 1

Status
Not open for further replies.

Melco001

Electrical
May 30, 2008
15
Can someone help me to adjust the protection values of the 27TN function in a GE UR G60 relay? I understand that it is the site where the third harmonic voltage data should be measured, from the generator neutral transformer.
 
Replies continue below

Recommended for you

If you register at SELINC.com, you can download the manual for the SEL-300G, which has an extensive procedure for calculations and fine tuning in the field. Further, SEL has a paper "Setting the 64G1 and 64G2 Elements in
SEL Generator Protection Relays", that goes into greater detail. Of course, you will have to translate the different settings names and operating principles between the two vendors.
 
I've never seen this protection work right, but to each his own if you get it to work.
 