"Sequential tripping" was employed on all eight of the 300 MW steam units in the first generating station I worked in. Its function essentially was to ensure that in situations where the trip request was not from operation of an electrical protection, a closed signal was received from all steam supply valves [plus open signals from the pair of units that had "release valves"] via limit switches before GSU breaker[s - ring bus configuration]] tripping was initiated. An electrical protection operation would trip the GSU breaker immediately, and I don't recall hearing of any situations where there was a catastrophic or even minor overspeed of any of the units under these conditions, ever.