Industrial
Mar 8, 2008
2
need help wiring a 2 speed motor 6 leads u v w x y z
what configuration for low and high speeds thanks
 
Replies continue below

Recommended for you

Try like this,

X Y Z-------Line
U V W-------Open SLOW SPEED



U V W--------Line
X Y Z--------Join Together HIGH SPEED



Hope this helps
 
is there any other configurations?
 
Yes, the first reply applies to constant torque application (Delta - Low speed Wye - High speed)

If it is a constant hp application, it would be Delta - High speed and Wye - Low speed.

You need to contact the motor supplier to know which connection is applicable (is there not a nameplate on this motor that tells you how to connect it for both speeds ?)

* Women are like the police. They can have all the evidence in the world and yet they still want a confession - Chris Rock *
 
Hi
your connections will depend on the type of windings in the motor....the above connections by kuldipkenya are for a motor with a tapped winding..which can be identified by a continuity test between your terminals...on this type of motor there will be a circuit between all 6 output leads!!!
the other type is a dual wound motor with two completely seperate windings!! ie..U V W and X Y Z with circuits between themselves only...u-v-w x-y-z and nothing between the two windings...
if that is the case , it is as simple as supplying one winding or the other....leaving the other windings open.

hope this helps