Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

3 PHASE DISTRIBUTION FEED WITH A REDUCED NEUTRAL

Status
Not open for further replies.

ED-GEE

Electrical
Mar 14, 2019
12
0
0
US
Can anyone clarify and show example of a 3 phase 400A feeder with a reduced size neutral? is that even allowed by NEC?
 
Replies continue below

Recommended for you

ED-GEE,
You need to find the unbalanced current first. But lets assume that you can connect a 400A single phase load on 3 phase 4 wire system, then your unbalanced load is 400A. NEC 220.61(B)(2) allows 70% on neutral current in excess of 200A. So your neutral current in this case will be 340A.
 
The transformer jumpers from the transformer terminals to the wye point connection carry the same current as the phases and should not be reduced in size.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.
Back
Top