I'd appreciate it for some feedback/explanation of the following occurance...
Presently there is a 3 phase 4 wire Y feeding a new subdivision at the end of the line with phase "a" and "c". On the way to the subdivision, there is a pump station with a 120/208 service that is radial fed. Before this there are 3 single phase reclosers that feed all of the above.
The issue: "a" phase recloser opens by a fault. The subdivision that is fed by this phase is not occupied, there are 4 empty houses with temp services and a worker complains that his tools are not working. 55v is measured at the transformer.
We investigated and found that the "a" phase was being backfed through a heating element in the pump station and continuing to the subdivision which virtually has no load besides the transformer it backfed through at the pump station and the transformer at the subdivision.
My explanation: is that because there is "no-load" at the subdivision, the breaker for the heating element will not trip and backfeed will continue until the heater is turned off or the other recloser is opened that is feeding the other phase of the pump station transformer.
Correct me if I'm wrong.
Thanks.
Presently there is a 3 phase 4 wire Y feeding a new subdivision at the end of the line with phase "a" and "c". On the way to the subdivision, there is a pump station with a 120/208 service that is radial fed. Before this there are 3 single phase reclosers that feed all of the above.
The issue: "a" phase recloser opens by a fault. The subdivision that is fed by this phase is not occupied, there are 4 empty houses with temp services and a worker complains that his tools are not working. 55v is measured at the transformer.
We investigated and found that the "a" phase was being backfed through a heating element in the pump station and continuing to the subdivision which virtually has no load besides the transformer it backfed through at the pump station and the transformer at the subdivision.
My explanation: is that because there is "no-load" at the subdivision, the breaker for the heating element will not trip and backfeed will continue until the heater is turned off or the other recloser is opened that is feeding the other phase of the pump station transformer.
Correct me if I'm wrong.
Thanks.