Is it possible for a 3phase motor to single phase during the time a bldg loses power on 1 leg untill the Emergency generator starts about 1 min from loss of power to generator start up and come on line?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Not to be OT, I guess it all depends on the size of the emergency generator. The most we got from a 2,000 kVA emergency generator was 1 min 42 seconds on startup!rasevskii said:"One minute for an emergency generator to start up and "come on line" is pretty long."
Very true. Big emergency generators do not qualify as a "legally required standby system" owing to its inherent longer starting time/ cutting-in.resqcapt19 said:"If it is a "legally required standby system", Article 701 requires it to be online within 60 seconds."
As Bill said, it depends.roydm said:Slightly off topic but wouldn't most three phase motor overload units trip on out of ballance with a phase missing?