gord99
Electrical
- Mar 7, 2002
- 3
This question may seem trivial but could someone confirm my reasoning? In a 3 phase wye-connected system, with voltages at 120/208v, and feeding a 'balanced' 3 phase 'purely resistive'load, the power can be calculated by summing the power from each phase winding of the transformer.
ie. P_total = 3 ( E_phase)(I_phase)
since E_phase = E_line/(root 3) and
I_phase = I_line, in a wye system, then:
P_total = 3 [E_line/(root 3)][I_line]
simplified, this becomes:
P_total = 360 (I_line)
when E_line = 208 volts.
So far so good. What happens when a balanced purely resistive load is connected across only two of the phase legs? As I see it, the total power should now be 2/3 of the 3 phase power.
ie. P_2phase = 2/3(360)(I_line) = 240(I_line)
Is this reasoning correct?
An example of this would be a feeder to one suite in an apartment where the 208 volts is derived across 2 x 120 volt phase legs of a 3 phase 120v/208v wye secondary. The balanced portion of this load would be connected across the 208 volts. I'm not concerned with the unbalanced loads at this point, which connect from phase to neutral.
ie. P_total = 3 ( E_phase)(I_phase)
since E_phase = E_line/(root 3) and
I_phase = I_line, in a wye system, then:
P_total = 3 [E_line/(root 3)][I_line]
simplified, this becomes:
P_total = 360 (I_line)
when E_line = 208 volts.
So far so good. What happens when a balanced purely resistive load is connected across only two of the phase legs? As I see it, the total power should now be 2/3 of the 3 phase power.
ie. P_2phase = 2/3(360)(I_line) = 240(I_line)
Is this reasoning correct?
An example of this would be a feeder to one suite in an apartment where the 208 volts is derived across 2 x 120 volt phase legs of a 3 phase 120v/208v wye secondary. The balanced portion of this load would be connected across the 208 volts. I'm not concerned with the unbalanced loads at this point, which connect from phase to neutral.