Yes, but that still amounts to the factor of sqrt3.
Phase angle is only important for calculating kW (or power factor).
The best is to look at an example:
Consider a 208Y/120V source and (3) loads of 10kW each at 208V. If they are connected to A-B, B-C and C-A lines respectively, they become a balanced circuit, connected in delta. The total load is 30kW.
Current in each 208V circuit is 10000/208=48A. This is the 'phase' current of the delta created by three loads.
You can calculate the 3 phase line amps using the 3 phase formula kVA= SQRT(3)*V(LL)*I(LL)/1000, which will be 83.2 amps (from A=1000*30/(1.732*208)
This is the same as what you will get by multiplying the 48A of 'phase' current, we calculated before, with Sqrt(3).
48A*Sqrt(3) = 83.2A.
If you have only two load circuits on, one of the line currents will be 83.2A and other two 48A each. Total real load 20kW.
If you have only one of the load circuits on, two of lines will have 48A each, the other will have 0A. Total real load 10kW.
So no phase angle is required to calculate kVA or amps.
However for kW, you need to take into account angle between the current and voltage you are using.
You may want to go through the exercises of considering the "black box" approach and calculate kVA and kW per phase. (Hint: L-N voltage is 30 degree out of phase with the line-line voltage).
Rafiq Bulsara