The system is fed by (3) 500kVA single phase transformers. each transformer's impedance is 3.4%, 240/120V.

primiary side: 12470/7200V.

the system is 208/120V and 3 phase.

My question is what the secondary KVA is and its impedance combined.

thank you very much,
 
Secondary, three times 500 KVA equals 1500 KVA.
PU impedance will be the same.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
IMG_6720_fuv5kc.jpg
 
and the main breaker of the system is only 2000A.

thanks
 
It appears that the main breaker is sized for 240/416 Volt use.

--------------------