mbk2k3
Electrical
- Nov 18, 2010
- 97
Hey guys,
Here is the islanded setup:
I have a 3 phase generator (with a NGR in its neutral) connected to a step-up transformer.
I asked for a DELTA-WYE transformer (delta on the generator side).
However the only available transformers are WYE-WYE.
I suspect I can't just leave the XO on the WYE side facing the generator floating/disconnected can I? I'm imagining issues with load imbalances causing current/voltage imbalances, and harmonics passing through the windings, etc.
I could connect an NGR on the XO of the tx as well, only downside is the the ground fault current would increase by an order of magnitude.
I def. can't solidly ground the XO as that would negate the NGR completely.
Am I missing anything else?