Hi, I am new to the forum and looking for some help with an air compressor control problem. I am trying to design a 3 wire stop start control station that will work with a single phase 240v starter.The problem lies with trying to maintain the coil circuit on the starter. I am using 3 wire start stop control to engage and seal the circuit which also runs through the pressure switch. Everytime the pressure switch opens, I loose the seal for the circuit and have to push the start button to start the compressor again. I can solve this by replacing the start stop with a simple toggle switch. Is it possible to use the 3 wire control without having to restart every time the pressure switch opens?