33 kV distributionsystem.

Status
Not open for further replies.

SauravWest

Electrical
Dec 4, 2019
35
0
0
NP
dear sirs,

i have to take 33 kV lines to different places for industry requiring 5 (nos) *30 = 150 MVA. i am concerned about the type of conductor to use.

i have read that we can use upto 165 mva in 33 kv. but dog conductor only has 324 amps. as line current.

regards,
 
Replies continue below

Recommended for you

Hi Saurav West,
1 x 30MVA = @ 33kV = 525Amp x 5 = 2625 Amps Goat ACSR conductor = 730amp
Would it not be feasible to step-up from sub 33 / 88kV OHL then stepdown at each 30MVA
 
150MVA at 33kV? What distance are we talking? What is the voltage drop??
I don't think it is feasible unless you are intending to take the power only a couple of kilometers.
 
What is dog and goat? Most conductors I run across at 34kV have bird names.

Smallest I have seen used is 2/0, but 4/0 is more typical of a rural distribution circuit.
 