mmiro227
Electrical
- Jan 29, 2002
- 2
We have a this site with three Caterpillar Generators that parallel. Two of them are 350kw and one is 300kw. Problem started when the third unti(350kw) was added. It is different pitch. The original two units are 15/16 pitch and the new unit is 2/3 pitch. To aliviate the third harmonics currents in the neutral, a reactor was added to this unit between neutral and ground. That solved the problem of circulating currents of this unit and the others when in parallel. The problem started when the 300kw, older unit, had to be replaced. A new generator was built to the exact 15/16 pitch of the original. Now there are neutral circulating currents between this unit and the others up to 400 amps when the unit is fully loaded. We know the problem are third harmonics according to test made with a VMI. Lifting the neutrals is not a viable solution in this case. Any ideas?
Thanks
Thanks