Hi Smoked,
Funny you mentioned resistance to voltage noise.
I came back home from a motor testing lab yesterday. Fairly large test rigs with 800 kW braking power. PWM and active front ends.
This is a very modern facility and there are all supervision, warnings and alarms you could think of - and then some.
Problem: The vibration transducers that are used to warn the operators if anything starts getting ugly (they cant hear anything because everything has been soundproofed and they are not allowed to enter the test cells when running the tests), these vibration transducers were live and kicking until they activated the brake motor (generator, as it is). The the 4-20 dropped below 4.00 mA and the warning went off.
It was the PWM residues on the signal cable that entered the current source output and probably got rectified inside so that the output current dropped below 4 mA. I could see it clearly on the scope. Remedy: 100 nF capacitor across transducer and 100 ohm resistors in both + and signal lines. So, that transducer got extra 2+2 V to feed. But since supply was 24 V and the load was 500 ohms, it worked.
Interesting side note. When I had fixed this problem, the next problem was that they got alarms from the transducer on the drive side. Too much vibration!
We will be looking at this more in depth next week. There are about fifteen such rigs on this site and all show low vibration amplitudes. We start to think that vibration is higher than indicated but that the EMI from PWM has taken the signal down a bit. That's why the one I fixed suddenly says vibration is high - perhaps...
But, otherwise, it is a convenient way of powering a transducer and also getting signal back in an easy-to-use form. Voltage drop is seldom an issue, so a 10 V signal does also work well. But then you mave common mode problems. Also, you cannot power the transducer via a two wire cable any more. But, I prefer 10 V. A lot easier to filter and also to trouble-shoot. No need to break the loop ur use other tricks. Just connect voltmeter and measure.
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...