bfdeleen
Electrical
- Jun 12, 2001
- 8
I have encountered the 4.8 kV, 60 Hz system for the first time and I cannot see an overall advantage to it compared to a 4.16 kV system. Circuit breakers come in maximum voltages of 4.76 and 8.25 kV, so the later is needed. Since there is a 4.8 kV generator, it is not inconceivable that it could operate slightly higher sometime. It begins to look like switchgear and wiring must be at 8.25 kV, even though the nominal system voltage is below 5 kV. Does anyone have previous experience with this voltage?