Not a simple question. There are several possible causes:
Here is an excerpt from
EASA Motor Root Cause Analsis:
"ROTOR SPARKING
There are several potential causes of rotor sparking on
fabricated rotors. Some are of a nondestructive nature, and
some can lead to rotor failure. (See Figure 5.)
Nondestructive sparking can and probably does occur
during normal motor operation. Such sparking is seldom
observed due to its low intensity and/or the motor enclosure
prohibits its observance. Normal operation can be defined
as any condition that could subject the motor to voltage dips,
load fluctuation, switching disturbances, etc. Sparking usu-ally
is not observed while running at full load. The centrifugal
force at full-load speed is usually greater than the electro-magnetic
forces acting on the bar, due to rated load current,
and tends to displace and hold the bar radially in the slot.
Furthermore, the frequency within the rotor circuit is very
low (equal to the slip frequency). This low frequency corre-
sponds to a low impedance of the rotor cage circuit, essen-tially
confining all rotor current to the cage itself. Therefore,
while possible, sparking is not normally observed during
operation at full load and speed.
During across-the-line starting, however, the current in
the rotor cage can be 5 to 7 times normal. This high current
combined with the higher cage impedance, due to the
frequency of the rotor current initially decaying from line
frequency at standstill, will cause a voltage drop along the
length of the bar in excess of 6 times the normal running
value. This voltage tends to send current through the
laminations. In effect, during start-up, there are actually two
parallel circuits—one through the rotor bar, and the other
through the laminations.
The magnetic forces created by the high current flow
during start-up cause the rotor bars to vibrate at a decaying
frequency, starting at line frequency, which produces a
force at twice line frequency. This tangential vibration within
the confines of the rotor slot causes intermittent interrup-tions
of the current flow between the bars and various
portions of the laminations with resultant visible arcing.
The rotor design and manufacturing processes include
measures intended to reduce sparking. However, material
and manufacturing tolerances, together with the effects of
differential thermal expansion and thermal cycling, pre-clude
any motor from “sparkless” operation. Even identical
or duplicate motors can and will exhibit differing levels of
spark intensity, since all component parts have tolerances
and are thermally cycled during operation.
The sparks observed in the air gap are actually very small
particles of bar and/or core iron, heated to incandescence
by current passing through the iron-bar boundary. Initial
punching burrs and/or particles of bar material removed
during installation can generally be expected to decrease
after several starts. However, particles generated by inter-mittent
sparking due to bar motion will not decrease during
the life of the motor.
The brief period of intensified sparking that can occur
during starting is not detrimental to motor life. Motors with
more than 20 years of operation have shown only slight
etching of the rotor bars at areas of contact with the core iron
when disassembled.
Destructive sparking can occur under several circum-stances,
the most common being a broken bar or a defective
bar-to-end ring connection.
Bars usually break near where the bar connects to the
end ring. Breakage is preceded by radial cracks starting
either in the top or bottom of the bar. While sparking caused
by fatigue failure of the rotor bar is usually greater in
intensity than that previously mentioned, it is still difficult to
visually detect since the majority of motor enclosures pre-vent
“line of sight” visual observation of the air gap.
Common methods of determining whether sparking is
caused by broken bars or end ring connections are:
• Visual inspection of the rotor assembly.
• Tapping the bars with a small hammer. Broken bars
have a dull sound, like a cracked bell. For loose bars,
tap one end of bar while feeling the opposite end for
movement.
• Current pulsation when the motor is under load.
• Single-phase rotational test.
• Growler test.
• Motor current signature analysis.
• Observed noise (rattling sound) during starting cycle.
• Audible cyclical noise.
Proper design, manufacture and operation of the motor
can prevent advanced levels of rotor sparking."