davva
Marine/Ocean
- Sep 27, 2004
- 99
I have read a passage in a text book that states "If the SWBD or MCC feeds equipment located in a hazardous area then a 4-pole circuit breaker should be used, as recommended in international standards".
There is no reference to the actually international standard where this "recommendation" stems from.
I have recently joined a company and their practice is to use a 3pole breaker with linked neutral bar at the distribution panel. The earth network usually being TN-S (separate neutral and protective earth). LV network 400V.
As the text book states it is only a recommendation I would like to get a feel for what the common practise is.
(I guess the source of the problem is that the neutral wire can rise to a potential above earth and create a spark hazard during maintenance?)
There is no reference to the actually international standard where this "recommendation" stems from.
I have recently joined a company and their practice is to use a 3pole breaker with linked neutral bar at the distribution panel. The earth network usually being TN-S (separate neutral and protective earth). LV network 400V.
As the text book states it is only a recommendation I would like to get a feel for what the common practise is.
(I guess the source of the problem is that the neutral wire can rise to a potential above earth and create a spark hazard during maintenance?)