Hi, this is an old subject several months ago, and I am revisiting it again.
I am beginning to see the benefit of a 3-pole switch in this particular application. Although I ask the contratcor to provide a 4-pole switch only to comply with the spec, he made a mistake a got a 3-pole switch, so I have drew up a diagram to for a 3-pole switch connection.
Becasue this is for a protable generator, I am wondering several things.
For example, when the maintenance staff do their periodic testing, while the commercial power is on, and you do not want to de-enegerize everything, is it safe to connect the neutral of the generator to the neutral service bus (in the disconnect switch in my diagram) while power is on? For this reason, is a 4-pole a better setup than a 3-pole and when the connection scheme seems clearly?
Also, any comment to the fused disconnect switch? Because the load panel EM is also protected, is that being redundant? A few of then staff has said to do away the disconnect switch. However I see the fused disconnect is serving to protect the load as an additional measure because the size of the portable genset and the ckt brk that protects the genset can vary, so I cannot rely on it alone.
The contractor also suggests to use disconnect because over in Japan here they have trouble finding the right fuse, as long as the trip item is faster than the load circuit breaker. Is that workable?
Bill, David, what is your opinion?