Good morning, I hope everyone is staying safe during Covid precautions.

To provide some background, my installation is in a school in Edmonton, Alberta, Canada. A Daikin RCS045D condensing unit with 4 compressors provides cooling and hot gas bypass if required. The condensing unit is internally wired for the possibility of 4 stages of cooling. The designer has only provided design for two line sets from the condensing unit to the air handler. Each line set comes with a liquid line solenoid. Each liquid and suction line is sized correctly for the two compressors operating concurrently. The supply air temperature is controlled by a BMS system. The BMS system will enable the Daikin unit.
Two questions:

1. Can I expect poor oil return if only 1 stage of cooling is energized?

2. Apart form the lack of efficiency operating with only 2 liquid line solenoids are there any other capacity issues I can expect.

Cheers,

Tom

 
Replies continue below

Recommended for you

The equipment manufacturer can tell you what piping options are possible. Oil return is one of their main considerations in writing up their guidelines.
 
Nowadays, digital compressors are specified in lieu of hot gas by-pass. check with your vendor.
 