Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

4-wire transmitter with 120Vac?

Status
Not open for further replies.

CuriousElectron

Electrical
Jun 24, 2017
182
Hi Gents,

I need to spec out a 4-20mA instrument that would come with a local 120VAC power supply. I'm measuring hydrostatic pressure at a remote site and need to bring 4-20mA signal back into the plant. No 24 Vdc available but 120VAC is available. Any recommendations for a brand?

Your typical GE Drucks and such all seem to be loop powered

Thanks,
EE
 
Replies continue below

Recommended for you

How 'remote' is this transmitter? Is there the option to run two-wire loop-powered, or provide 24V power via a spare pair? Can you provide a small PSU 120V/24V locally and use a standard transmitter?

I'm sure you've considered these possibilities, but you haven't explained why they won't work.
 
Not understanding..? This is what loop powered devices are for. Power it from the place that wants the data over the 4-20mA line. That's why it's 4mA not 0-20mA.

Keith Cress
kcress -
 
Different options to consider. Sometimes equipment does not come with its own power supply and you have to purchase one separately. Another thing to consider, is if the equipment takes 24 VDC but you only have 120 VAC at the site, you can buy a power supply that takes 120 VAC and outputs 24 VDC. Another option, is having a small enclosure or junction box located remotely where you take care of the power supplies and most of the wiring. Then just run a cable/wire bundle from the junction box to your equipment.
 