rcw retired EE
Electrical
- Jul 21, 2005
- 907
We are bidding a spec for a plant in the Mid-east that requires a disconnect switch in the neutral ground of the 400 kV transformers, 375 MVA, 400 kV-18.5kv, YNd11. The intent is to allow 400 kV system operation grounded or ungrounded. No reason given.
Can the neutral insulation level be reduced? If so, is there a good resource to calculate the suggested Neutral Point BIL? Full level is about 1425 kV, minimum for an impedance grounded neutral is 350 kv. (C57.12.00)
At 400 kV, full insulation appears impractical. Is this a common requirement? Is 400 kV ungrounded an actual operating condition? We think it may be a specification carry over from 220 kV systems where ungraded insulation is practical.
Can the neutral insulation level be reduced? If so, is there a good resource to calculate the suggested Neutral Point BIL? Full level is about 1425 kV, minimum for an impedance grounded neutral is 350 kv. (C57.12.00)
At 400 kV, full insulation appears impractical. Is this a common requirement? Is 400 kV ungrounded an actual operating condition? We think it may be a specification carry over from 220 kV systems where ungraded insulation is practical.