400V Supply on 380V motor

Status
Not open for further replies.

electronext

Electrical
Jan 4, 2010
11
MY
will there be any long time effect if we connect 380V 60Hz motor to 400V 60Hz supply?

Thank you.
 
Replies continue below

Recommended for you

400V 60Hz was the clients requirement and yes it is not a common voltage here in the Philippines. The motor was designed with triple voltage 220/380/440V 60Hz.

Are those effects will still happen even if the motor has 5% voltage tolerance?
 
My guess is that you are actually in luck. Probably actually about a 205/410V motor with that name plant. 380V is less than 8% down at 380 and less than 8% up at 440V. Those three voltage probably only involve two different connections.
 
the motor connection are delta-delta/wye-wye/delta 220/380/440V respectively.

 
the motor connection are delta-delta/wye-wye/delta 220/380/440V respectively.
Then you don't have a problem at all! Connect the motor for 400V operation. Since you have a double-delta connection for 220V - change the connection to double-wye (1.732X220 = 380V), about 5% over(400/380).
 