eeprom
Electrical
- May 16, 2007
- 482
Hi,
I have two pumps, both 500 Hp, running on VFDs or across the line in bypass mode. Both motors have a history of failing windings. Both motors are inverter rated. There are no RTDs on either. Both motors are within 150ft of their VFDs, and neither motor is using VFD cabling. Both motors have two breaker in series. Breaker 1 is in a GE MCC and has a GE microversatrip with long and ground protection. Both long time settings are about 1.15X with a trip time of 5 seconds at 6X, both ground trips are set to 100A. Breaker 2 is an ABB LI breaker, with the long set at 1.2X FLA and the I set to 8X plug rating, which comes out to 6400A. Downstream of the ABB breaker are contactors for VFD operation and across the line starting. The VFD also has fuses internal.
Recently, motor #2 tripped twice on overload while running at a very low mechanical load. The trip was occurring in breaker 1 in the GE breaker in the MCC. The relay indicated the overload element had tripped. We meggered the motor and everything appeared to be fine. I did not get the megger readings, but there were in the hundreds of megs.
We started the pump (motor #2) up again, in bypass mode, and kept it at low load while we measured the phase currents. They were about 105% of the FLA, and there was some imbalance, about 2%. The pump was running at about 1/5 or 1/6 of it's rated load, but the motor was drawing more than it's FLA.
I asked to switch pumps so we could see what that current reading on motor 1 would be for the same mechanical load. However, that motor (motor 1) tripped upon starting, also in bypass mode. Again it was the GE relay that tripped, not the ABB. I did not see this, but I was told it tripped immediately. According to the GE relay settings, to trip immediately had to be caused by the ground fault element. The GE relay has no short time element, and the instantaneous element has been turned off.
We meggered motor 1 and it came in around 500 megs on all phases. We meggered again including the cables from the output contactor down to the motor and got the same. Phase to phase measurements were all similar, around 0.6 ohms DC resistance, but the meter used is not very accurate at that low of a reading. This is a fluke 287, and I don't think it's accurate to 0.1 ohms at that load. The calculated impedance of the motor windings, operating at pf of 0.84, results in a per winding impedance of 0.492/_32. Therefore I believe the fluke readings are reasonably valid.
We then tried hand rotating the pump and it rotated easily. There is no binding.
This is as far as I got. I can detect no ground fault, but it appears we are tripping on a ground fault. Motor 1 won't start because it faults. Motor 2 is running in its service factor while operating at 20% of its load. What I believe is that the motor windings are being deteriorated by spiking from the VFDs. As the winding insulation breaks down, some of the windings become shorted, and it then takes more current to create the same torque. The increased current causes heating, further breaking down the insulation, and then eventual failure.
This is happening to both motors. It seems it has be to related to the VFDs. However I cannot find anything wrong. What I am hoping for from the forum is someone who can help me calculate how spiking and reflected waves can shorten motor life. Or, point me in another direction.
Thanks for your help.
I have two pumps, both 500 Hp, running on VFDs or across the line in bypass mode. Both motors have a history of failing windings. Both motors are inverter rated. There are no RTDs on either. Both motors are within 150ft of their VFDs, and neither motor is using VFD cabling. Both motors have two breaker in series. Breaker 1 is in a GE MCC and has a GE microversatrip with long and ground protection. Both long time settings are about 1.15X with a trip time of 5 seconds at 6X, both ground trips are set to 100A. Breaker 2 is an ABB LI breaker, with the long set at 1.2X FLA and the I set to 8X plug rating, which comes out to 6400A. Downstream of the ABB breaker are contactors for VFD operation and across the line starting. The VFD also has fuses internal.
Recently, motor #2 tripped twice on overload while running at a very low mechanical load. The trip was occurring in breaker 1 in the GE breaker in the MCC. The relay indicated the overload element had tripped. We meggered the motor and everything appeared to be fine. I did not get the megger readings, but there were in the hundreds of megs.
We started the pump (motor #2) up again, in bypass mode, and kept it at low load while we measured the phase currents. They were about 105% of the FLA, and there was some imbalance, about 2%. The pump was running at about 1/5 or 1/6 of it's rated load, but the motor was drawing more than it's FLA.
I asked to switch pumps so we could see what that current reading on motor 1 would be for the same mechanical load. However, that motor (motor 1) tripped upon starting, also in bypass mode. Again it was the GE relay that tripped, not the ABB. I did not see this, but I was told it tripped immediately. According to the GE relay settings, to trip immediately had to be caused by the ground fault element. The GE relay has no short time element, and the instantaneous element has been turned off.
We meggered motor 1 and it came in around 500 megs on all phases. We meggered again including the cables from the output contactor down to the motor and got the same. Phase to phase measurements were all similar, around 0.6 ohms DC resistance, but the meter used is not very accurate at that low of a reading. This is a fluke 287, and I don't think it's accurate to 0.1 ohms at that load. The calculated impedance of the motor windings, operating at pf of 0.84, results in a per winding impedance of 0.492/_32. Therefore I believe the fluke readings are reasonably valid.
We then tried hand rotating the pump and it rotated easily. There is no binding.
This is as far as I got. I can detect no ground fault, but it appears we are tripping on a ground fault. Motor 1 won't start because it faults. Motor 2 is running in its service factor while operating at 20% of its load. What I believe is that the motor windings are being deteriorated by spiking from the VFDs. As the winding insulation breaks down, some of the windings become shorted, and it then takes more current to create the same torque. The increased current causes heating, further breaking down the insulation, and then eventual failure.
This is happening to both motors. It seems it has be to related to the VFDs. However I cannot find anything wrong. What I am hoping for from the forum is someone who can help me calculate how spiking and reflected waves can shorten motor life. Or, point me in another direction.
Thanks for your help.