We have had a EM 2200kva 6 pole turbine driven generator in our shop for repair with which we are having a problem.
The unit came in for repair with a low ground reading on the wound rotor (.3 meg ohms). We cleaned and varnish treated the rotor and got it to come up to 4200 MOhms. We assembled the generator and applied 4160v to the stator so we could run it up to speed to test for vibration (rotor leads open). After this testing was completed the rotor was found to be near 0 meg again. We cut open the connections on the rotor to isolate which coil or coils were grounded and found them to be the 2 lead poles.(the 6 poles are connected 1 circuit series).
We rewound and reassembled the rotor. Final testing indicated 200 Gigohms @ 1000v. Again we applied 4160v to the stator so we could run it up to speed to test for vibration (rotor leads open). After a brief run time we started to smell something burning and powered the unit down. Again the rotor was 0 Megohms. We cut open the coil interconnections to isolate the grounded pole or poles and found that, again, the 2 lead coils were grounded.
I guess my question is, could we be damaging the rotor winding by trying to run this generator as if it were a motor and if so why?
The unit came in for repair with a low ground reading on the wound rotor (.3 meg ohms). We cleaned and varnish treated the rotor and got it to come up to 4200 MOhms. We assembled the generator and applied 4160v to the stator so we could run it up to speed to test for vibration (rotor leads open). After this testing was completed the rotor was found to be near 0 meg again. We cut open the connections on the rotor to isolate which coil or coils were grounded and found them to be the 2 lead poles.(the 6 poles are connected 1 circuit series).
We rewound and reassembled the rotor. Final testing indicated 200 Gigohms @ 1000v. Again we applied 4160v to the stator so we could run it up to speed to test for vibration (rotor leads open). After a brief run time we started to smell something burning and powered the unit down. Again the rotor was 0 Megohms. We cut open the coil interconnections to isolate the grounded pole or poles and found that, again, the 2 lead coils were grounded.
I guess my question is, could we be damaging the rotor winding by trying to run this generator as if it were a motor and if so why?