newbie here
recently got a new reduced voltage starter for our 4160V 400HP motor at our plant. doesn't work.
single phase transformers, 167,167,&250 kva. i can "hear" a two stage start(reduced voltage and full voltage). the motor is a rebuild from corporate stock in North Carolina (we are in Michigan).
contracted engineer for the contractor we hired for this says current waveform imbalance from mismached transformers(OK, i'll buy that), undersized transformers, autotransformer to big(he designed), and no damper on fan to reduce load. oh, he also says motor is not a 400hp but could be a 500hp.(autotransformer to big?)
i myself could not reduce timer to get autotransformer completely out of circuit, still comes on for two seconds (crawling around inside by the buss makes me nervous). after that the motor takes another 14.9 seconds to come up to full speed. draws about 250A, nameplate is 48.
the wierd thing...if i start it with the autotransformer in the circuit with (his) recommended start of 30s. then A phase will draw about 80A (250kva trans), B & C draw about 67A (167kva trans) then the run contactor pulls in.... and then the multilin then will shut everything down on excessive acceleration time
kinda new to this whole voltage class, any suggestions would be appreciated...thanx
recently got a new reduced voltage starter for our 4160V 400HP motor at our plant. doesn't work.
single phase transformers, 167,167,&250 kva. i can "hear" a two stage start(reduced voltage and full voltage). the motor is a rebuild from corporate stock in North Carolina (we are in Michigan).
contracted engineer for the contractor we hired for this says current waveform imbalance from mismached transformers(OK, i'll buy that), undersized transformers, autotransformer to big(he designed), and no damper on fan to reduce load. oh, he also says motor is not a 400hp but could be a 500hp.(autotransformer to big?)
i myself could not reduce timer to get autotransformer completely out of circuit, still comes on for two seconds (crawling around inside by the buss makes me nervous). after that the motor takes another 14.9 seconds to come up to full speed. draws about 250A, nameplate is 48.
the wierd thing...if i start it with the autotransformer in the circuit with (his) recommended start of 30s. then A phase will draw about 80A (250kva trans), B & C draw about 67A (167kva trans) then the run contactor pulls in.... and then the multilin then will shut everything down on excessive acceleration time
kinda new to this whole voltage class, any suggestions would be appreciated...thanx