itsmoked
Electrical
- Feb 18, 2005
- 19,114
A generator had been setup to run a facility and had run it many times.
The facility toasted as I mentioned elsewhere. Now they are reconnecting the generator to temporarily run some of the functional remains.
The "industrial" electricians are seeking permission to "ground the generator's neutral" at the generator. The generator has only ever had it's ground lug grounded and the three phases hooked to the facility, never a neutral.
It's a Volvo Penta.
I've never looked in the connection compartment. Would there normally be a neutral? I was assuming the generator was built delta.
If there is no actual neutral star point in the windings is there a problem grounding the 'neutral' lug?
If there actually is a star point in the windings that is connected to the neutral lug is there any reason why it shouldn't be bonded as the sole source for the building?
Keith Cress
kcress -
The facility toasted as I mentioned elsewhere. Now they are reconnecting the generator to temporarily run some of the functional remains.
The "industrial" electricians are seeking permission to "ground the generator's neutral" at the generator. The generator has only ever had it's ground lug grounded and the three phases hooked to the facility, never a neutral.
It's a Volvo Penta.
I've never looked in the connection compartment. Would there normally be a neutral? I was assuming the generator was built delta.
If there is no actual neutral star point in the windings is there a problem grounding the 'neutral' lug?
If there actually is a star point in the windings that is connected to the neutral lug is there any reason why it shouldn't be bonded as the sole source for the building?
Keith Cress
kcress -