xnuke
Electrical
- May 3, 1999
- 1,029
A source typically connected to a 480 V bus requires 480 V sensing from the 480 V line side of the main breaker for grid synchronization purposes. For a proposed application however, the source will be connected via a step-up transformer to connect to a 13.2 kV bus with a 13.2 kV line feeding the main breaker. Normal 120 V secondary sensing from a 13.2 kV:120 V VT is not an option; the source vendor still requires sensing at 480 V. Are either of these viable options for this one-off project:
[ol 1]
[li]Get custom VTs made with 480 V secondaries[/li]
[li]Use standard 13.2 kV:120 V VTs with 120 V secondaries, then connect 480:120 V VTs backwards to the normal secondaries in a step-up fashion to provide the 480 V[/li]
[/ol]
Please describe advantages and disadvantages for either, or provide other viable options. Whatever the solution, it has to fit into the MV switchgear.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.