Hi,
I am at a large convention center that has forty 4000 amp 480/277 main switch boards.
Each main switch board is feed from an independent utility owned 12kv to 480/277 transformer.
The transformer has no lightning protection on the secondary side. The main switch board has a N-G main bonding jumper and a TVSS .
Four times in the last two years on different switch boards, the TVSS units have failed in a catastrophic fashion. A lot smoke, some minor internal switch board damage, a completely destroyed TVSS unit and a main breaker trip. Of course management is not too impressed when guests have to be evactuated , fire department has to respond, and power cannot be restored until the TVSS unit is gutted and the switch board internals inspected for damage.
Here’s the interesting part. It is not the MOV’s failing. In fact in all four cases the MOV’s and the sand surrounding the MOV’s are in good shape with no damage. (But all the fuses did open).
Both the manufacturer and an independent R&D center have confirmed this. Instead the arc blasts seem to becoming from facing energized lug connections and fuses that feed the TVSS.
These are year 2000 model TVSS units that (by design) had no insulating barrier between the input lugs, and the TVSS’s disconnect switch input lugs are connected with unprotected #4 awg copper wire directly to the switch board bus. The entire TVSS unit consisting of a disconnect, fuses and TVSS unit is mounted by the manufacturer internal to the switch board. Newer models of this style TVSS have fiber insulation barriers between all exposed energized metal parts.
The manufacturer is going to offer their ideas sometime in the future and we are going to work with the power utility on power quality testing. Both of these are going to be drawn out events that will take us well into peak show season.
I would like some advice on making some meaningful short-term solutions to reduce the potential for the phase to phase arc blast while the engineers come up with a permanent solution.
My plan is to wrap the lugs and fuses with medium voltage insulation sheeting and ty-rap it in place.
Questions:
Is there any technical down side to this?
Would this prevent the arcing?
What type of insulation would be best, both from ease of installing and from insulation qualities?
A retailer name would be great. All I find are importers selling to OEM's.
Any type of material I should avoid? (rubber?)
Any comments or advice will be much appreciated.
Thanks,
Andy
I am at a large convention center that has forty 4000 amp 480/277 main switch boards.
Each main switch board is feed from an independent utility owned 12kv to 480/277 transformer.
The transformer has no lightning protection on the secondary side. The main switch board has a N-G main bonding jumper and a TVSS .
Four times in the last two years on different switch boards, the TVSS units have failed in a catastrophic fashion. A lot smoke, some minor internal switch board damage, a completely destroyed TVSS unit and a main breaker trip. Of course management is not too impressed when guests have to be evactuated , fire department has to respond, and power cannot be restored until the TVSS unit is gutted and the switch board internals inspected for damage.
Here’s the interesting part. It is not the MOV’s failing. In fact in all four cases the MOV’s and the sand surrounding the MOV’s are in good shape with no damage. (But all the fuses did open).
Both the manufacturer and an independent R&D center have confirmed this. Instead the arc blasts seem to becoming from facing energized lug connections and fuses that feed the TVSS.
These are year 2000 model TVSS units that (by design) had no insulating barrier between the input lugs, and the TVSS’s disconnect switch input lugs are connected with unprotected #4 awg copper wire directly to the switch board bus. The entire TVSS unit consisting of a disconnect, fuses and TVSS unit is mounted by the manufacturer internal to the switch board. Newer models of this style TVSS have fiber insulation barriers between all exposed energized metal parts.
The manufacturer is going to offer their ideas sometime in the future and we are going to work with the power utility on power quality testing. Both of these are going to be drawn out events that will take us well into peak show season.
I would like some advice on making some meaningful short-term solutions to reduce the potential for the phase to phase arc blast while the engineers come up with a permanent solution.
My plan is to wrap the lugs and fuses with medium voltage insulation sheeting and ty-rap it in place.
Questions:
Is there any technical down side to this?
Would this prevent the arcing?
What type of insulation would be best, both from ease of installing and from insulation qualities?
A retailer name would be great. All I find are importers selling to OEM's.
Any type of material I should avoid? (rubber?)
Any comments or advice will be much appreciated.