We are installing a new extrusion line and I got schematics from the OEM. The first thing that caught my eye is the value of the xformer. 55KVA primary overcurrent device 150amp breaker. THe values they give me are 388 Fla on the 240v side. Their formula is 388/3phase=129.3anps.So 240*129.3*1.73=53.7KVA.I thought 240*388*1.73/1000=161KVA xformer.My question is why are they dividing by 3 when their is no phase to nuetral voltage. The know values I have are 75210watts for total heater band values at 327.14amps. SO 240*327.14*1.73/1000=135.8KVA. With these values a 150KVA be correct? Also is secondary overcurrent protection nessacary for delta delta xfromers since the oem is already not providing?