power2engineer
Electrical
- May 18, 2003
- 53
We have a 2.5 MVA 13.8KV (Y-G)/ 480V (Y-G) Utility power supplying power to Schneider Electric 4000A, 480V, 3 Ph, 4W QED6 Main Switchboard with MTZ breakers.
Building major loads Panels and other DG Sources are connected to this Main switchboard bus with their respective breakers.
One of the feeder is connecting 300KW, 480V, 3Ph BESS system (Manufacturer SOCOMEC) Feeder with 800A circuit breaker with Ground fault trip set at 160A Zero time delay.
This BESS system feeder breaker we experience frequent ground fault trip especially when there is heavy rains.
We did megger the BESS system feeder cables and found no insulation failure.
BESS system manual allows connection of BESS system to Phase, 4W system with Neutral and Ground bonded which is what our system.
Does anybody have any experience what may be the cause of this BESS Feeder breaker keeps tripping on Ground fault.
Please see system SLD file attachment.
Thanks for sharing your learned opinion.
Building major loads Panels and other DG Sources are connected to this Main switchboard bus with their respective breakers.
One of the feeder is connecting 300KW, 480V, 3Ph BESS system (Manufacturer SOCOMEC) Feeder with 800A circuit breaker with Ground fault trip set at 160A Zero time delay.
This BESS system feeder breaker we experience frequent ground fault trip especially when there is heavy rains.
We did megger the BESS system feeder cables and found no insulation failure.
BESS system manual allows connection of BESS system to Phase, 4W system with Neutral and Ground bonded which is what our system.
Does anybody have any experience what may be the cause of this BESS Feeder breaker keeps tripping on Ground fault.
Please see system SLD file attachment.
Thanks for sharing your learned opinion.